1
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A lightning stroke discharges impulse current of $$10$$ kA (peak) on a $$400$$ kV transmission line having surge impedance of $$250\,\Omega $$. The magnitude of transient over-voltage traveling waves in either direction assuming equal distribution form the point of lightning strike will be
A
$$1250$$ kV
B
$$1650$$ kV
C
$$2500$$ kV
D
$$2900$$ kV
2
GATE EE 2003
MCQ (Single Correct Answer)
+2
-0.6
A dc distribution system is shown in figure with load currents as marked. The two ends of the feeder are fed by voltage sources such that $${V_P} - {V_Q} = 3V.$$ the value of the voltage $${V_P}$$ for a minimum voltage of $$220$$ $$V$$ at any point along the feeder is GATE EE 2003 Power System Analysis - Parameters and Performance of Transmission Lines Question 46 English
A
$$225.89$$ $$V$$
B
$$222.89$$ $$V$$
C
$$220.0$$ $$V$$
D
$$228.58$$ $$V$$
3
GATE EE 2003
MCQ (Single Correct Answer)
+2
-0.6
A balanced delta connected load of $$\left( {8 + j6} \right)\Omega $$ per phase is connected to a $$400$$ $$V$$, $$50$$ $$Hz$$, $$3-$$phase supply lines. If the input power factor is to be improved to $$0.9$$ by connecting a bank of star connected capacitors the required KVAR of the bank is
A
$$42.7$$
B
$$10.2$$
C
$$28.8$$
D
$$39.4$$
4
GATE EE 2003
MCQ (Single Correct Answer)
+2
-0.6
A surge of 20 kV magnitude travels along a lossless cable towards its junction with two identical lossless overhead transmission lines. The inductance and the capacitance of the cable are 0.4 mH and 0.5 $$\mu F$$ per km. The inductance and capacitance of the overhead transmission lines are 1.5 mH and 0.015 $$\mu F$$ per km. The magnitude of the voltage at the junction due to surge is
A
36.72 kV
B
18.36 kV
C
6.07 kV
D
33.93 kV