1
GATE EE 2017 Set 2
Numerical
+2
-0
A 3-phase 50 Hz generator supplies power of 3 MW at 17.32 kV to a balanced 3-phase inductive load through an overhead line. The per phase line resistance and reactance are 0.25 $$\Omega $$ and 3.925 $$\Omega $$ respectively. If the voltage at the generator terminal is 17.87 kV, the power factor of the load is ________.
Your input ____
2
GATE EE 2017 Set 1
MCQ (Single Correct Answer)
+2
-0.6
A load is supplied by a $$230$$ $$V,$$ $$50$$ $$Hz$$ source. The active power $$P$$ and the reactive power $$Q$$ consumed by the load are such that $$1$$ $$kW$$ $$ \le P \le 2\,kW\,\,$$ and $$\,1\,\,kVAR \le 2\,\,kVAR.\,\,$$ A capacitor connected across the load for power factor correction generates $$1$$ $$kVAR$$ reactive power. The worst case power factor after power factor correction is
A
$$0.447$$ lag
B
$$0.707$$ lag
C
$$0.894$$ lag
D
$$1$$
3
GATE EE 2016 Set 1
Numerical
+2
-0
A three-phase cable is supplying $$800$$ kW and $$600$$ kVAr to an inductive load. It is intended to supply an additional resistive load of $$100$$ kW through the same cable without increasing the heat dissipation in the cable, by providing a three-phase bank of capacitors connected in star across the load. Given the line voltage is $$3.3$$ kV, $$50$$ Hz, the capacitance per phase of the bank expressed in microfarads, is ________.
Your input ____
4
GATE EE 2016 Set 1
Numerical
+2
-0
A single-phase transmission line has two conductors each of 10 mm radius. These are fixed at a center-to-center distance of 1 m in a horizontal plane. This is now converted to a three-phase transmission line by introducing a third conductor of the same radius. This conductor is fixed at an equal distance D from the two single-phase conductors. The three-phase line is fully transposed. The positive sequence inductance per phase of the three phase system is to be 5% more than that of the inductance per conductor of the single phase system. The distance D, in meters, is ________.
Your input ____