1
GATE EE 1999
MCQ (Single Correct Answer)
+2
-0.6
A 3-phase, 11 kV, 50 Hz, 200 kW load has a power factor of 0.8 lag. A delta connected 3-phase capacitor is used to improve the power factor to unity. The capacitance power phase of the capacitor in micro-farads is
A
3.948
B
1.316
C
0.439
D
11.844
2
GATE EE 1999
MCQ (Single Correct Answer)
+2
-0.6
A single phase AC distributor supplies two single phase loads as shown in figure. The voltage drop from A to C is GATE EE 1999 Power System Analysis - Parameters and Performance of Transmission Lines Question 50 English
A
4.5 V
B
31.5 V
C
30 V
D
20 V
3
GATE EE 1999
MCQ (Single Correct Answer)
+2
-0.6
$$A$$ $$220$$ kV, $$20$$ km long, $$3$$-phase transmission line has the following $$A, B, C, D$$ constants. $$A=D=0.96$$$$\angle {3^0},$$ $$\,B = 55\angle {65^0}\,\,\Omega /$$ phase, $$\,C = 0.5 \times {10^{ - 4}}\angle {90^0}\,\,$$ $$S/$$phase. Its correct charging current per phase is
A
$$11/\sqrt 3 \,\,A$$
B
$$11$$ $$A$$
C
$$220$$ $$A$$
D
$$220/\sqrt 3 A.$$
4
GATE EE 1998
MCQ (Single Correct Answer)
+2
-0.6
A shunt reactor of $$100$$ MVAR is operated at $$98$$% of its rated voltage and $$96$$% of its rated frequency. The reactive power absorbed by the reactor is;
A
$$98$$ MVAR
B
$$104.02$$ MVAR
C
$$96.04$$ MVAR
D
$$100.04$$ MVAR