1
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A 500 MVA, 50 Hz, 3-phase turbo-generator produces power at 22 kV. Generator is Y-connected and its neutral is solidly grounded. Its sequence reactances are X1 = X2 = 0.15 and X0 = 0.05 pu. it is operating at rated voltage and disconnected from the rest of the system (no load). The magnitude of the sub-transient line current for single line ground fault at the generator terminal in pu will be
A
2.851
B
3.333
C
6.667
D
8.553
2
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A $$3$$-phase generator rated at $$110$$ MVA, $$11$$ kV is connected through circuit breakers to a transformer. The generator is having direct axis sub-transient reactance $$X'{'_d} = 19\% ,\,\,$$ transient reactance $$X{'_d} = 26\% \,\,$$ and synchronous reactance $$=130$$%. The generator is operating at no load and rated voltage when a three phase short circuit fault occurs between the breakers and the transformer. The magnitude of initial symmetrical rims current in the breakers will be
A
$$4.44$$ kA
B
$$22.20$$ kA
C
$$30.39$$ kA
D
$$38.45$$ kA
3
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A 3-phase transmission line supplies $$\Delta - $$ connected load Z. The conductor $$'c'$$ of the line develops an open circuit fault as shown in figure. The currents in the lines are as shown on the diagram. The +ve sequence current component in line 'a' will be GATE EE 2004 Power System Analysis - Symmetrical Components and Symmetrical and Unsymmetrical Faults Question 26 English
A
$$5.78\,\angle \, - {30^ \circ }$$
B
$$5.78\,\angle \, - {90^ \circ }$$
C
$$6.33\,\angle \, - {90^ \circ }$$
D
$$10.00\,\angle \, - {30^ \circ }$$
4
GATE EE 2003
MCQ (Single Correct Answer)
+2
-0.6
A 20-MVA, 6.6-kV, 3-phase alternator is connected to a 3-phase transmission line. The per unit positive sequence, negative sequence and zero sequence impedance of the alternator are j0.1, and j0.04 respectively. The neutral of the alternator is connected to ground through an inductive reactor of j0.05 p.u. The per unit positive, negative and zero sequence impedances of the transmission line are j0.1 and j0.3 respectively. All per unit values are based on the machine ratings. A solid ground fault occurs at one phase of the far end of the transmission line. The voltage of the alternator neutral with respect to ground during the fault is
A
513.8 V
B
889.9 V
C
1112.0 V
D
642.2 V