1
GATE EE 2003
MCQ (Single Correct Answer)
+2
-0.6
A 20-MVA, 6.6-kV, 3-phase alternator is connected to a 3-phase transmission line. The per unit positive sequence, negative sequence and zero sequence impedance of the alternator are j0.1, and j0.04 respectively. The neutral of the alternator is connected to ground through an inductive reactor of j0.05 p.u. The per unit positive, negative and zero sequence impedances of the transmission line are j0.1 and j0.3 respectively. All per unit values are based on the machine ratings. A solid ground fault occurs at one phase of the far end of the transmission line. The voltage of the alternator neutral with respect to ground during the fault is
A
513.8 V
B
889.9 V
C
1112.0 V
D
642.2 V
2
GATE EE 2002
MCQ (Single Correct Answer)
+2
-0.6
A generator is connected to a transformer which feeds another transformer through a short feeder. The zero sequence impedance values are expressed in pu on a common base and are indicated in figure. The Thevenin equivalent zero sequence impedance at point B is GATE EE 2002 Power System Analysis - Symmetrical Components and Symmetrical and Unsymmetrical Faults Question 30 English
A
0.8 + j0.6
B
0.75 + j0.22
C
0.75 + j0.25
D
1.5 + j0.25
3
GATE EE 2001
MCQ (Single Correct Answer)
+2
-0.6
A $$50$$ Hz alternator is rated $$500$$ $$MVA,$$ $$20$$ $$kV,$$ with $${X_d} = 1.0$$ per unit and $$X'{'_d} = 0.2$$ per unit. It supplies a purely resistive load of $$400$$ $$MW$$ at $$20$$ $$kV.$$ The load is connected directly across the generator terminals when a symmetrical fault occurs at the load terminals. The initial rms current in the generator in per units is
A
$$7.22$$
B
$$6.4$$
C
$$3.22$$
D
$$2.2$$
4
GATE EE 2000
MCQ (Single Correct Answer)
+2
-0.6
The severity of line-to-ground and three phase faults at the terminals of an unloaded synchronous generator is to be same. If the terminal voltage is
$$1.0$$ p.u. and $${Z_1} = {Z_2} = j0.1\,\,$$ p.u.,
$$\,{Z_0} = j0.05\,\,\,\,\,$$ p.u., for the alternator, then the required inductive reacttance for neutral grounding is
A
$$0.0166$$ p.u.
B
$$0.05$$ p.u.
C
$$0.1$$ p.u.
D
$$0.15$$ p.u.