-0.6
A $$50$$ Hz alternator is rated $$500$$ $$MVA,$$ $$20$$ $$kV,$$ with $${X_d} = 1.0$$ per unit and $$X'{'_d} = 0.2$$ per unit. It supplies a purely resistive load of $$400$$ $$MW$$ at $$20$$ $$kV.$$ The load is connected directly across the generator terminals when a symmetrical fault occurs at the load terminals. The initial rms current in the generator in per units is
2
GATE EE 2000
MCQ (Single Correct Answer)
+2
-0.6
The severity of line-to-ground and three phase faults at the terminals of an unloaded synchronous generator is to be same. If the terminal voltage is
$$1.0$$ p.u. and $${Z_1} = {Z_2} = j0.1\,\,$$ p.u.,
$$\,{Z_0} = j0.05\,\,\,\,\,$$ p.u., for the alternator, then the required inductive reacttance for neutral grounding is
$$1.0$$ p.u. and $${Z_1} = {Z_2} = j0.1\,\,$$ p.u.,
$$\,{Z_0} = j0.05\,\,\,\,\,$$ p.u., for the alternator, then the required inductive reacttance for neutral grounding is
3
GATE EE 1998
MCQ (Single Correct Answer)
+2
-0.6
For the network shown in figure the zero sequence reactances in p.u. are indicated. The zero sequence driving point reactance of the node 3 is