1
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
The generalized circuit constants of a $$3$$-phase, $$220$$ $$kV$$ rated voltage, medium length transmission line are $$A = D = 0.936 + j\,0.016 = 0.936\angle {0.98^ \circ }$$
$$B = 33.5 + j138 = 142.0\angle {76.4^ \circ }\,\Omega $$
$$\,C = \left( { - 5.18 + j914} \right) \times \,{10^{ - 6}}\,\Omega $$
If the load at the receiving end is $$50$$ MW at $$220$$ $$kV$$ with a power factor of 0.9 lagging, then magnitude of line to line sending end voltage should be
A
$$133.23$$ $$kV$$
B
$$220.00$$ $$kV$$
C
$$230.78$$ $$kV$$
D
$$246.30$$ $$kV$$
2
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A $$800$$ $$kV$$ transmission line is having per phase line inductance of $$1.1$$ $$mH/km$$ and per phase line capacitance of $$11.68$$ $$nF/km.$$ Ignoring the length of the line, its ideal power transfer capability in $$MW$$ is
A
$$1204$$ $$MW$$
B
$$1504$$ $$MW$$
C
$$2085$$ $$MW$$
D
$$2606$$ $$MW$$
3
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A $$110$$ $$kV,$$ single core coaxial, XLPE insulated power cable delivering power at $$50$$ $$Hz,$$ has a capacitance of $$125$$ $$nF/km.$$ If the dielectric loss tangent of XLPE is $$\,2\,\, \times \,\,{10^{ - 4}},$$ the dielectric power loss in this cable in $$W/km$$ is
A
$$5.0$$
B
$$31.7$$
C
$$37.8$$
D
$$189.0$$
4
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A lightning stroke discharges impulse current of $$10$$ kA (peak) on a $$400$$ kV transmission line having surge impedance of $$250\,\Omega $$. The magnitude of transient over-voltage traveling waves in either direction assuming equal distribution form the point of lightning strike will be
A
$$1250$$ kV
B
$$1650$$ kV
C
$$2500$$ kV
D
$$2900$$ kV

GATE EE Subjects

Browse all chapters by subject