A 3-phase transformer has rating of 20 MVA, 220 kV (star) / 33 kV (delta) with leakage reactance of 12%. The transformer reactance (in ohms) referred to each phase of the L.V. delta-connected side is
A
23.5
B
19.6
C
18.5
D
8.7
2
GATE EE 2001
MCQ (Single Correct Answer)
+2
-0.6
The hysteresis loop of a magnetic material has an area of 5 cm2 with the scales given as 1 cm = 2 AT and 1 cm = 50 mWb. At 50 Hz, the total hysteresis loss is
A
15 W
B
20 W
C
25 W
D
50 W
3
GATE EE 2000
MCQ (Single Correct Answer)
+2
-0.6
A 3-phase delta/star transformer is supplied at 6000 V on the delta-connected side. The terminal voltage on the secondary side when supplying full load as 0.8 lagging power-factor is 415 V. The equivalent resistance and reactance drops for the transformer are 1% and 5% respectively. The turn's ratio of the transformer is:
A
14
B
24
C
42
D
20
4
GATE EE 1999
MCQ (Single Correct Answer)
+2
-0.6
A 10 kVA, 400 V/200 V, single phase transformer with a percentage resistance of 3% and percentage reactance of 6% is supplying a current of 50 A to a resistive load. The value of the load voltage is:
A
194 V
B
390 V
C
192 V
D
196 V