GATE EE 2017 Set 1
Numerical
+2
-0
A three-phase, three winding $$\triangle$$ / $$\triangle$$ / Y (1.1 kV/6.6 kV/400 V) transformer is energized from AC
mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV
winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line
current in ampere drawn by the 1.1 kV winding from the mains is _______.
Your input ____
2
GATE EE 2016 Set 2
MCQ (Single Correct Answer)
+2
-0.6
Three single-phase transformers are connected to form a delta-star three-phase transformer of
110 kV/ 11 kV. The transformer supplies at 11 kV a load of 8 MW at 0.8 p.f. lagging to a nearby
plant. Neglect the transformer losses. The ratio of phase currents in delta side to star side is
3
GATE EE 2016 Set 2
Numerical
+2
-0
A single-phase, 2 kVA, 100/200 V transformer is reconnected as an auto-transformer such that its kVA rating is maximum. The new rating, in kVA, is ______.
Your input ____
4
GATE EE 2016 Set 1
Numerical
+2
-0
A single-phase 400 V, 50 Hz transformer has an iron loss of 5000 W at the condition. When
operated at 200 V, 25 Hz, the iron loss is 2000 W. When operated at 416 V, 52 Hz, the value of the
hysteresis loss divided by the eddy current loss is ________.
Your input ____