1
GATE EE 2015 Set 1
Numerical
+2
-0
Two single-phase transformers T1 and T2 each rated at 500 kVA are operated in parallel. Percentage impedances of T1 and T2 are (1 + j6) and (0.8 + j4.8), respectively. To share a load of 1000 kVA at 0.8 lagging power factor, the contribution of T2 (in kVA) is ________.
Your input ____
2
GATE EE 2015 Set 1
Numerical
+2
-0
A 200/400 V, 50 Hz, two-winding transformer is rated at 20 kVA. Its windings are connected as an auto-transformer of rating 200/600 V. A resistive load of 12 Ω is connected to the high voltage (600 V) side of the auto-transformer. The value of equivalent load resistance (in Ohm) as seen from low voltage side is _____.
Your input ____
3
GATE EE 2015 Set 2
MCQ (Single Correct Answer)
+2
-0.6
A balanced (positive sequence) three-phase AC voltage source is connected to a balanced, star connected load through a star-delta transformer as shown in the figure. The line-to-line voltage rating is 230 V on the star side, and 115 V on the delta side. If the magnetizing current is neglected and $${\overline{\mathrm I}}_\mathrm s=100\angle0^\circ$$, then what is the value of $${\overline{\mathrm I}}_\mathrm p$$ in Ampere?


4
GATE EE 2015 Set 2
Numerical
+2
-0
Two three-phase transformers are realized using single-phase transformers as shown in the figure.
The phase difference (in degree) between voltages V1 and V2 is _______.
The phase difference (in degree) between voltages V1 and V2 is _______.Your input ____
GATE EE Subjects
Browse all chapters by subject
Digital Electronics
Control Systems
Power System Analysis
Analog Electronics
Electric Circuits
Electrical and Electronics Measurement
Power Electronics
Electromagnetic Fields
Signals and Systems
Electrical Machines
Engineering Mathematics
General Aptitude