1
GATE EE 1997
MCQ (Single Correct Answer)
+2
-0.6
A voltage $$V=400$$ sin $$314.16t$$ is applied to a $$1$$-phase transformer on no-load. If the no load current of the transformer is $$2\sin \left( {314.16t - {{85}^0}} \right),\,\,$$ then magnetization branch impedance will be approximately
A
$$141\,\,\angle 90$$
B
$$200\,\,\angle - 85$$
C
$$200\,\,\angle 85$$
D
$$282\,\,\angle - 80$$
2
GATE EE 1997
Numerical
+2
-0
A $$3$$-phase transformer bank consists of three identical $$2300/230$$ $$V,$$ $$15$$ $$kVA$$ single-phase transformers connected in delta/delta. The bank supplies a $$20$$ $$kVA,$$ unity $$p.f.$$ $$3$$-phase load. If one of the single-phase transformer develops a fault, and is removed, the load carried by each of the two transformers now operating in open delta will be __________$$kVA.$$
Your input ____
3
GATE EE 1993
MCQ (Single Correct Answer)
+2
-0.6
A $$220/440$$ $$V,$$ $$50$$ $$Hz$$ single phase transformer operates on $$220$$ $$V,$$ $$40$$ $$Hz$$ supply with secondary winding. Then
A
the eddy current loss and hysteresis loss of the transformer decrease
B
the eddy current loss and hysteresis loss of the transformer increase
C
the hysteresis loss of the transformer increases while eddy current loss remains the same
D
the hysteresis loss remains the same whereas eddy current loss decreases