1
GATE EE 2014 Set 3
Numerical
+2
-0
The load shown in the figure absorbs 4 kW at a power factor of 0.89 lagging. GATE EE 2014 Set 3 Electrical Machines - Transformers Question 64 English Assuming the transformer to be ideal, the value of the reactance X to improve the input power factor to unity is ___________.
Your input ____
2
GATE EE 2014 Set 1
MCQ (Single Correct Answer)
+2
-0.6
The core loss of a single phase, 230/115 V, 50 Hz power transformer is measured from 230 V side by feeding the primary (230 V side) from a variable voltage variable frequency source while keeping the secondary open circuited. The core loss is measured to be 1050 W for 230 V, 50 Hz input. The core loss is again measured to be 500W for 138 V, 30 Hz input. The hysteresis and eddy current losses of the transformer for 230 V, 50 Hz input are respectively.
A
508 W and 542 W
B
468 W and 582 W
C
498 W and 552 W
D
488 W and 562 W
3
GATE EE 2013
MCQ (Single Correct Answer)
+2
-0.6
The following arrangement consists of an ideal transformer and an attenuator which attenuates by a factor of 0.8. An ac voltage VWX1 = 100V is applied across WX to get an open circuit voltage VYZ1 across YZ. Next, an ac voltage VYZ2 =100V is applied across YZ to get an open circuit voltage VWX2 across WX. Then, $$\frac{V_{YZ1}}{V_{WX1}}$$, $$\frac{V_{WX2}}{V_{YZ2}}$$ are respectively, GATE EE 2013 Electrical Machines - Transformers Question 60 English
A
125/100 and 80/100
B
100/100 and 80/100
C
100/100 and 100/100
D
80/100 and 80/100
4
GATE EE 2012
MCQ (Single Correct Answer)
+2
-0.6
A single phase 10 kVA, 50 Hz transformer with 1 kV primary winding draws 0.5 A and 55 W, at rated voltage and frequency, on no load. A second transformer has a core with all its linear dimensions $$\sqrt2$$ times the corresponding dimensions of the first transformer. The core material and lamination thickness are the same in both transformers. The primary windings of both the transformers have the same number of turns. If a rated voltage of 2 kV at 50 Hz is applied to the primary of the second transformer, then the no load current and power, respectively, are
A
0.7 A, 77.8 W
B
0.7 A, 155.6 W
C
1 A, 110 W
D
1 A, 220 W