1
GATE EE 2009
MCQ (Single Correct Answer)
+2
-0.6
GATE EE 2009 Electrical Machines - Transformers Question 26 English

The figure above shows coil $$1$$ and $$2,$$ with dot markings as shown, having $$4000$$ and $$6000$$ turns respectively. Both the coils have a rated current of $$25$$ $$A.$$ Coil $$1$$ is excited with single phase, $$400$$ $$V,$$ $$50$$ $$Hz$$ supply.

The coils are to be connected to obtain a single-phase, $${{400} \over {1000}}\,\,V,$$ auto-transformer to drive a load of $$10$$ $$kVA.$$ Which of the options given should be exercised to realize the required auto-transformer?

A
Connect $$A$$ and $$D;$$ Common $$B$$
B
Connect $$B$$ and $$D;$$ Common $$C$$
C
Connect $$A$$ and $$C;$$ Common $$B$$
D
Connect $$A$$ and $$C;$$ Common $$D$$
2
GATE EE 2008
MCQ (Single Correct Answer)
+2
-0.6
The core of two-winding transformer is subjected to a magnetic flux variation as indicated in the figure. GATE EE 2008 Electrical Machines - Transformers Question 21 English 1 GATE EE 2008 Electrical Machines - Transformers Question 21 English 2

The induced $$emf$$ $$\left( {{e_{rs}}} \right)$$ in the secondary winding as a function of time will be of the form

A
GATE EE 2008 Electrical Machines - Transformers Question 21 English Option 1
B
GATE EE 2008 Electrical Machines - Transformers Question 21 English Option 2
C
GATE EE 2008 Electrical Machines - Transformers Question 21 English Option 3
D
GATE EE 2008 Electrical Machines - Transformers Question 21 English Option 4
3
GATE EE 2008
MCQ (Single Correct Answer)
+2
-0.6
Three single-phase transformers are connected to form a $$3$$-phase transformer bank. The transformers are connected in the following manner. GATE EE 2008 Electrical Machines - Transformers Question 24 English

The transformer connection will be represented by

A
$$Yd0$$
B
$$Yd1$$
C
$$Yd6$$
D
$$Yd11$$
4
GATE EE 2007
MCQ (Single Correct Answer)
+2
-0.6
A single-phase $$50$$ $$kVA,$$ $$250$$ $$V/500V$$ two winding transformer has an efficiency of $$95\% $$ at full load, unity power factor. If it is reconfigured as a $$500V/750V$$ auto-transformer, its efficiency at its new rated load at unity power factor will be
A
$$95.752\% $$
B
$$97.851\% $$
C
$$98.276\% $$
D
$$99.241\% $$