1
GATE EE 2006
MCQ (Single Correct Answer)
+2
-0.6
Two transformers are to be operated in parallel such that they share load in proportion to their $$kVA$$ ratings. The rating of the first transformer is $$500$$ $$kVA$$ and its $$pu$$ leakage impedance is $$0.05$$ $$pu.$$ If the rating of second transformer is $$250$$ $$kVA,$$ its $$pu$$ leakage impedance is
A
$$0.20$$
B
$$0.10$$
C
$$0.25$$
D
$$0.025$$
2
GATE EE 2006
MCQ (Single Correct Answer)
+2
-0.6
A $$300$$ $$kVA$$ transformer has $$95\% $$ efficiency at full load $$0.8$$ $$pf$$ lagging and $$96\% $$ efficiency at half load, unity $$pf.$$

The iron loss $$\left( {{P_i}} \right)$$ in $$kW,$$ under full load operation are

A
$${P_c} = 4.12,\,\,{P_i} = 8.51$$
B
$${P_c} = 6.59,\,\,{P_i} = 9.21$$
C
$${P_c} = 8.51,\,\,{P_i} = 4.12$$
D
$${P_c} = 12.72,\,\,{P_i} = 3.07$$
3
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
The resistance and reactance of a 100 kVA 11000|400 V, $$\triangle$$ - Y distribution transformer are 0.02 and 0.07 pu respectively. The phase impedance of the transformer referred to the primary is
A
(0.02 + j0.07) Ω
B
(0.55 + j1.925) Ω
C
(15.125 + j52.94) Ω
D
(72.6 + j254.1) Ω
4
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A 500 kVA, 3-phase transformer has iron loses of 300 W and full load copper losses of 600 W. The percentage load at which the transformer is expected to have maximum efficiency is
A
50.0%
B
70.7%
C
141.4%
D
200.0%