1
GATE EE 2015 Set 2
Numerical
+2
-0
The incremental costs (in rupees/$$MWh$$) of operating two generating units are functions of their respective powers $${P_1}$$ and $${P_2}$$ in $$MW,$$ and are given by $$${{d{C_1}} \over {d{P_1}}} = 0.2{P_1} + 50$$$ $$${{d{C_2}} \over {d{P_2}}} = 0.24{P_2} + 40$$$
Where, $$$\eqalign{ & 20\,MW \le {P_1} \le 150\,MW \cr & 20\,MW \le {P_2} \le 150MW. \cr} $$$
For a certain load demand, $${P_1}$$ and $${P_2}$$ have been chosen such that $$\,\,d{C_1}/d{P_1} = 76\,Rs/MWh\,\,$$ and $$\,d{C_2}/d{P_2} = 68.8\,Rs/MWh.\,\,$$ If the generations are rescheduled to minimize the total cost, then $${P_2}$$ is ____________.
Your input ____
2
GATE EE 2014 Set 1
MCQ (Single Correct Answer)
+2
-0.6
The fuel cost functions of two power plants are
Plant $${P_1}:\,{C_1} = 0.05\,Pg_1^2 + AP{g_1} + B$$
Plant $${P_2}:\,{C_2} = 0.10\,Pg_2^2 + 3AP{g_2} + 2B$$
Where, $$P{g_1}$$ and $$P{g_2}$$ are the generator powers of two plants and $$A$$ and $$B$$ are the constants. If the two plants optimally share $$1000$$ $$MW$$ load at incremental fuel cost of $$100$$ $$Rs/MWh,$$ the ratio of load shared by plants $${P_1}$$ and $${P_2}$$ is
A
$$1:4$$
B
$$2:3$$
C
$$3:2$$
D
$$4:1$$
3
GATE EE 2011
MCQ (Single Correct Answer)
+2
-0.6
A load center of 120 MW derives power from two power stations connected by 220 kV transmission lines of 25 km and 75 km as shown in the figure below. The three generators G1,G2 and G3 are of 100 MW capacity each and have identical fuel cost characteristics. The minimum loss generation schedule for supplying the 120 MW load is GATE EE 2011 Power System Analysis - Power Generation Cost Question 12 English
A
$$P1 = 80\,MW + $$ losses
$$P2 = 20\,MW$$
$$P3 = 20\,MW + $$ losses
B
$$P1 = 60\,MW $$
$$P2 = 30\,MW$$ $$+$$ losses
$$P3 = 30\,MW $$
C
$$P1 = 40\,MW $$
$$P2 = 40\,MW$$
$$P3 = 40\,MW + $$ losses
D
$$P1 = 30\,MW + $$ losses
$$P2 = 45\,MW$$
$$P3 = 45\,MW $$
4
GATE EE 2009
MCQ (Single Correct Answer)
+2
-0.6
Three generators are feeding a load of $$100$$ $$MW$$. The details of the generators Rating, Efficiency and Regulation are shown below GATE EE 2009 Power System Analysis - Power Generation Cost Question 13 English

In the event of increased load power demand, which of the following will happen?

A
All the generators will share equal power
B
Generator-$$3$$ will share more power compared to Generator-$$1$$
C
Generator-$$1$$ will share more power compared to Generator-$$2$$
D
Generator-2 will share more power compared to Generator-$$3$$

GATE EE Subjects

Browse all chapters by subject