1
GATE EE 2000
MCQ (Single Correct Answer)
+2
-0.6
The incremental cost characteristic of two generators delivering $$200$$ $$MW$$ are as follows $$\,\,\,{{d{F_1}} \over {d{P_1}}} = 20 + 0.1{P_1},\,\,{{d{F_2}} \over {d{P_2}}} = 16 + 0.2{P_2}$$
For economic operation, the generations $${P_1}$$ and $${P_2}$$ should be
A
$${P_1} = {P_2} = 100\,MW$$
B
$${P_1} = 80MW,\,\,{P_2} = 120\,MW$$
C
$${P_1} = 200MW,\,\,{P_2} = 0\,MW$$
D
$${P_1} = 120MW,\,\,{P_2} = 80\,MW$$
2
GATE EE 1999
MCQ (Single Correct Answer)
+2
-0.6
An industrial consumer has a daily load pattern of $$2000$$ $$kW$$, $$0.8$$ lag for $$12$$ Hrs. and $$1000$$ $$kW$$ $$UPF$$ for $$12$$ Hrs. The load factor is
A
$$0.5$$
B
$$0.75$$
C
$$0.6$$
D
$$2.0$$