1
GATE EE 2006
MCQ (Single Correct Answer)
+2
-0.6
A $$300$$ $$kVA$$ transformer has $$95\% $$ efficiency at full load $$0.8$$ $$pf$$ lagging and $$96\% $$ efficiency at half load, unity $$pf.$$

The iron loss $$\left( {{P_i}} \right)$$ in $$kW,$$ under full load operation are

A
$${P_c} = 4.12,\,\,{P_i} = 8.51$$
B
$${P_c} = 6.59,\,\,{P_i} = 9.21$$
C
$${P_c} = 8.51,\,\,{P_i} = 4.12$$
D
$${P_c} = 12.72,\,\,{P_i} = 3.07$$
2
GATE EE 2006
MCQ (Single Correct Answer)
+2
-0.6
A $$300$$ $$kVA$$ transformer has $$95\% $$ efficiency at full load $$0.8$$ $$pf$$ lagging and $$96\% $$ efficiency at half load, unity $$pf.$$

What is the maximum efficiency (in %) at unity $$pf$$ load?

A
$$95.1$$
B
$$96.2$$
C
$$96.4$$
D
$$98.1$$
3
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
The resistance and reactance of a 100 kVA 11000|400 V, $$\triangle$$ - Y distribution transformer are 0.02 and 0.07 pu respectively. The phase impedance of the transformer referred to the primary is
A
(0.02 + j0.07) Ω
B
(0.55 + j1.925) Ω
C
(15.125 + j52.94) Ω
D
(72.6 + j254.1) Ω
4
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A 50 kVA, 3300/230 V single-phase transformers is connected as an autotransformer shown in figure. The nominal rating of the autotransformer will be GATE EE 2004 Electrical Machines - Transformers Question 60 English
A
50.0 kVA
B
53.5 kVA
C
717.4 kVA
D
767.4 kVA