1
GATE EE 2018
Numerical
+2
-0
A 3-phase 900 kVA, 3 kV / $$\sqrt 3 $$ kV (Δ/Y), 50 Hz transformer has primary (high voltage side) resistance per phase of 0.3 Ω and secondary (low voltage side) resistance per phase of 0.02 Ω. Iron loss of the transformer is 10 kW. The full load % efficiency of the transformer operated at unity power factor is _______ (up to 2 decimal places).
Your input ____
2
GATE EE 2017 Set 2
Numerical
+2
-0
If the primary line voltage rating is 3.3 kV (Y side) of a 25 kVA. $$Y-\triangle$$ transformer (the per phase turns ratio is 5:1), then the line current rating of the secondary side (in Ampere) is_______.
Your input ____
3
GATE EE 2017 Set 1
Numerical
+2
-0
A three-phase, three winding $$\triangle$$ / $$\triangle$$ / Y (1.1 kV/6.6 kV/400 V) transformer is energized from AC mains at the 1.1 kV side. It supplies 900 kVA load at 0.8 power factor lag from the 6.6 kV winding and 300 kVA load at 0.6 power factor lag from the 400 V winding. The RMS line current in ampere drawn by the 1.1 kV winding from the mains is _______.
Your input ____
4
GATE EE 2016 Set 2
MCQ (Single Correct Answer)
+2
-0.6
Three single-phase transformers are connected to form a delta-star three-phase transformer of 110 kV/ 11 kV. The transformer supplies at 11 kV a load of 8 MW at 0.8 p.f. lagging to a nearby plant. Neglect the transformer losses. The ratio of phase currents in delta side to star side is
A
1 : 10$$\sqrt 3 $$
B
10$$\sqrt 3 $$ : 1
C
1 : 10
D
$$\sqrt 3 $$ : 10