1
GATE EE 2015 Set 2
MCQ (Single Correct Answer)
+2
-0.6
The synchronous generator shown in the figure is supplying active power to an infinite bus via two short, lossless transmission lines, and is initially in steady state. The mechanical power input to the generator and the voltage magnitude E are constant. If one line is tripped at time t1 by opening the circuit breakers at the two ends (although there is no fault), then it is seen that the generator undergoes a stable transient. Which one of the following waveforms of the rotor angle $$\delta $$ shows the transient correctly? GATE EE 2015 Set 2 Power System Analysis - Power System Stability Question 12 English
A
GATE EE 2015 Set 2 Power System Analysis - Power System Stability Question 12 English Option 1
B
GATE EE 2015 Set 2 Power System Analysis - Power System Stability Question 12 English Option 2
C
GATE EE 2015 Set 2 Power System Analysis - Power System Stability Question 12 English Option 3
D
GATE EE 2015 Set 2 Power System Analysis - Power System Stability Question 12 English Option 4
2
GATE EE 2014 Set 3
Numerical
+2
-0
The figure shows the single line diagram of a single machine infinite bus system. GATE EE 2014 Set 3 Power System Analysis - Power System Stability Question 14 English

The inertia constant of the synchronous generator $$𝐻 = 5$$ $$MW-s/MVA.$$ Frequency is $$50Hz.$$ Mechanical power is $$1$$ pu. The system is operating at the stable equilibrium point with rotor angle $$\delta $$ equal to $${30^ \circ }$$. A three phase short circuit fault occurs at a certain location on one of the circuits of the double circuit transmission line. During fault, electrical power in pu is $$\,{P_{\max }}\,\,\sin \delta .\,\,\,$$. If the values of $$\delta $$ and $$d$$$$\delta $$$$/dt$$ at the instant of fault clearing are $${45^ \circ }$$ and $$3.762$$ radian/s respectively, then $$\,{P_{\max }}$$ (in pu) is _________.

Your input ____
3
GATE EE 2012
MCQ (Single Correct Answer)
+2
-0.6
A cylindrical rotor generator delivers $$0.5$$ pu power in the steady-state to an infinite bus through a transmission line of reactance $$0.5$$ pu. The generator no-load voltage is $$1.5$$ pu and the infinite bus voltage is $$1$$ pu. The inertia constant of the generator is $$5$$ $$MW-s/MVA$$ and the generator reactance is $$1$$ pu. The critical clearing angle, in degrees, for a three-phase dead short circuit fault at the generator terminal is
A
$$53.5$$
B
$$60.2$$
C
$$70.8$$
D
$$79.6$$
4
GATE EE 2009
MCQ (Single Correct Answer)
+2
-0.6
A $$500$$ $$MW,$$ $$21$$ $$kV,$$ $$50$$ $$Hz,$$ $$3$$-phase, $$2$$-pole synchronous generator having a rated $$p.f.=$$$$0.9,$$ has a moment of inertia $$\,\,27.5\,\, \times \,\,{10^3}\,\,kg\,\,{m^2}.\,\,$$ The inertia constant $$(H)$$ will be
A
$$2.44$$ s
B
$$2.71$$ s
C
$$4.88$$ s
D
$$5.42$$ s