1
GATE EE 2015 Set 1
Numerical
+2
-0
A 50 Hz generating unit has H-constant of 2 MJ/MVA. The machine is initially operating in steady state at synchronous speed, and producing 1 pu of real power. The initial value of the rotor angle $$\delta $$ is $${5^ \circ }$$, when a bolted three phase to ground short circuit fault occurs at the terminal of the generator. Assuming the input mechanical power to remain at 1 pu, the value of $$\delta $$ in degrees, 0.02 second after the fault is _____________
Your input ____
2
GATE EE 2015 Set 2
MCQ (Single Correct Answer)
+2
-0.6
The synchronous generator shown in the figure is supplying active power to an infinite bus via two short, lossless transmission lines, and is initially in steady state. The mechanical power input to the generator and the voltage magnitude E are constant. If one line is tripped at time t1 by opening the circuit breakers at the two ends (although there is no fault), then it is seen that the generator undergoes a stable transient. Which one of the following waveforms of the rotor angle $$\delta $$ shows the transient correctly?
3
GATE EE 2014 Set 3
Numerical
+2
-0
The figure shows the single line diagram of a single machine infinite bus system.
The inertia constant of the synchronous generator $$𝐻 = 5$$ $$MW-s/MVA.$$ Frequency is $$50Hz.$$ Mechanical power is $$1$$ pu. The system is operating at the stable equilibrium point with rotor angle $$\delta $$ equal to $${30^ \circ }$$. A three phase short circuit fault occurs at a certain location on one of the circuits of the double circuit transmission line. During fault, electrical power in pu is $$\,{P_{\max }}\,\,\sin \delta .\,\,\,$$. If the values of $$\delta $$ and $$d$$$$\delta $$$$/dt$$ at the instant of fault clearing are $${45^ \circ }$$ and $$3.762$$ radian/s respectively, then $$\,{P_{\max }}$$ (in pu) is _________.
Your input ____
4
GATE EE 2012
MCQ (Single Correct Answer)
+2
-0.6
A cylindrical rotor generator delivers $$0.5$$ pu power in the steady-state to an infinite bus through a transmission line of reactance $$0.5$$ pu. The generator no-load voltage is $$1.5$$ pu and the infinite bus voltage is $$1$$ pu. The inertia constant of the generator is $$5$$ $$MW-s/MVA$$ and the generator reactance is $$1$$ pu. The critical clearing angle, in degrees, for a three-phase dead short circuit fault at the generator terminal is
GATE EE Subjects
Browse all chapters by subject
Electric Circuits
Electrical Machines
Engineering Mathematics
Signals and Systems
Power Electronics
Power System Analysis
Digital Electronics
Analog Electronics
Electromagnetic Fields
Control Systems
Electrical and Electronics Measurement
General Aptitude