1
GATE EE 2012
MCQ (Single Correct Answer)
+2
-0.6
A cylindrical rotor generator delivers $$0.5$$ pu power in the steady-state to an infinite bus through a transmission line of reactance $$0.5$$ pu. The generator no-load voltage is $$1.5$$ pu and the infinite bus voltage is $$1$$ pu. The inertia constant of the generator is $$5$$ $$MW-s/MVA$$ and the generator reactance is $$1$$ pu. The critical clearing angle, in degrees, for a three-phase dead short circuit fault at the generator terminal is
A
$$53.5$$
B
$$60.2$$
C
$$70.8$$
D
$$79.6$$
2
GATE EE 2009
MCQ (Single Correct Answer)
+2
-0.6
A $$500$$ $$MW,$$ $$21$$ $$kV,$$ $$50$$ $$Hz,$$ $$3$$-phase, $$2$$-pole synchronous generator having a rated $$p.f.=$$$$0.9,$$ has a moment of inertia $$\,\,27.5\,\, \times \,\,{10^3}\,\,kg\,\,{m^2}.\,\,$$ The inertia constant $$(H)$$ will be
A
$$2.44$$ s
B
$$2.71$$ s
C
$$4.88$$ s
D
$$5.42$$ s
3
GATE EE 2008
MCQ (Single Correct Answer)
+2
-0.6
A lossless single machine infinite bus power system is shown below: GATE EE 2008 Power System Analysis - Power System Stability Question 18 English

The synchronous generator transfers $$1.0$$ per unit of power to the infinite bus. The critical clearing time of circuit breaker is $$0.28$$ s. If another identical synchronous generator is connected in parallel to the existing generator and each generator is scheduled to supply $$0.5$$ per unit of power, then the critical clearing time of the circuit breaker will

A
Reduce to $$0.14$$ s
B
Reduce but will be more than $$0.14$$ s
C
Remain constant at $$0.28$$ s
D
Increase beyond $$0.28$$ s
4
GATE EE 2007
MCQ (Single Correct Answer)
+2
-0.6
Consider a synchronous generator connected to an infinite bus by two identical parallel transmission lines. The transient reactance $$x'$$ of the generator $$0.1$$ pu. Due to some previous disturbance, the rotor angle $$(d)$$ is undergoing an undamped oscillation, with the maximum value of $$\delta \left( t \right)$$ equal to $$\,{130^ \circ }\,.$$ One of the parallel lines trip due to relay mal-operation at an instant $$\,\,\,\,\,$$ when $$\,\delta \left( t \right)\,\, = {130^ \circ }\,\,$$ as shown in the figure. The maximum value of the per unit line reactance $$x,$$ such that the system does not lose synchronism subsequent to this tripping is GATE EE 2007 Power System Analysis - Power System Stability Question 19 English
A
0.87
B
0.74
C
0.67
D
0.54
GATE EE Subjects
EXAM MAP
Medical
NEETAIIMS
Graduate Aptitude Test in Engineering
GATE CSEGATE ECEGATE EEGATE MEGATE CEGATE PIGATE IN
Civil Services
UPSC Civil Service
Defence
NDA
Staff Selection Commission
SSC CGL Tier I
CBSE
Class 12