1
GATE EE 2015 Set 1
Numerical
+2
-0
A 200/400 V, 50 Hz, two-winding transformer is rated at 20 kVA. Its windings are connected as an auto-transformer of rating 200/600 V. A resistive load of 12 Ω is connected to the high voltage (600 V) side of the auto-transformer. The value of equivalent load resistance (in Ohm) as seen from low voltage side is _____.
Your input ____
2
GATE EE 2015 Set 1
Numerical
+2
-0
Two single-phase transformers T1 and T2 each rated at 500 kVA are operated in parallel. Percentage impedances of T1 and T2 are (1 + j6) and (0.8 + j4.8), respectively. To share a load of 1000 kVA at 0.8 lagging power factor, the contribution of T2 (in kVA) is ________.
Your input ____
3
GATE EE 2014 Set 2
MCQ (Single Correct Answer)
+2
-0.6
For a single phase, two winding transformer, the supply frequency and voltage are both
increased by 10%. The percentage changes in the hysteresis loss and eddy current loss,
respectively are
4
GATE EE 2014 Set 1
MCQ (Single Correct Answer)
+2
-0.6
The core loss of a single phase, 230/115 V, 50 Hz power transformer is measured from 230 V
side by feeding the primary (230 V side) from a variable voltage variable frequency source
while keeping the secondary open circuited. The core loss is measured to be 1050 W for
230 V, 50 Hz input. The core loss is again measured to be 500W for 138 V, 30 Hz input. The
hysteresis and eddy current losses of the transformer for 230 V, 50 Hz input are respectively.
GATE EE Subjects
Browse all chapters by subject
Electric Circuits
Electrical Machines
Engineering Mathematics
Signals and Systems
Power Electronics
Power System Analysis
Digital Electronics
Analog Electronics
Electromagnetic Fields
Control Systems
Electrical and Electronics Measurement
General Aptitude