1
GATE EE 2011
MCQ (Single Correct Answer)
+2
-0.6
Two generator units $$G1$$ and $$G2$$ are connected by $$15$$ $$kV$$ line with a bus at the mid-point as shown below GATE EE 2011 Power System Analysis - Per Unit System Question 5 English
$${G_1} = 250\,\,MVA.\,\,\,15kV,\,\,$$ positive sequence $$X = 25$$% on its own base
$${G_2} = 100\,\,MVA.\,\,\,15kV,\,$$ positive sequence $$X = 10$$% on its own base
$${L_1}$$ and $${L_2}$$ $$= 10$$ $$km,$$ positive sequence $$ X = 0.225$$ $$\,\,\Omega /km$$

For the above system, the positive sequence diagram with the p.u values on the $$100$$ $$MVA$$ common

A
GATE EE 2011 Power System Analysis - Per Unit System Question 5 English Option 1
B
GATE EE 2011 Power System Analysis - Per Unit System Question 5 English Option 2
C
GATE EE 2011 Power System Analysis - Per Unit System Question 5 English Option 3
D
GATE EE 2011 Power System Analysis - Per Unit System Question 5 English Option 4
2
GATE EE 2011
MCQ (Single Correct Answer)
+2
-0.6
Two generator units $$G1$$ and $$G2$$ are connected by $$15$$ $$kV$$ line with a bus at the mid-point as shown below GATE EE 2011 Power System Analysis - Per Unit System Question 4 English
$${G_1} = 250\,\,MVA.\,\,\,15kV,\,\,$$ positive sequence $$X = 25$$% on its own base
$${G_2} = 100\,\,MVA.\,\,\,15kV,\,$$ positive sequence $$X = 10$$% on its own base
$${L_1}$$ and $${L_2}$$ $$= 10$$ $$km,$$ positive sequence $$ X = 0.225$$ $$\,\,\Omega /km$$

In the above system the three-phase fault $$MVA$$ at the bus $$3$$ is

A
$$82.55$$ $$MVA$$
B
$$85.11$$ $$MVA$$
C
$$170.91$$ $$MVA$$
D
$$181.82$$ $$MVA$$
3
GATE EE 2010
MCQ (Single Correct Answer)
+2
-0.6
For the power system shown in the figure below, the specifications of the components are the following:
$$G1: 25$$ $$kV,$$ $$100$$ $$MVA,$$ $$X=9$$%
$$G2: 25$$ $$kV,$$ $$100$$ $$MVA,$$ $$X=9$$%
$$T1: 25$$ $$kV/220$$ $$kV,$$ $$90$$ $$MVA,$$ $$X=12$$%
$$T2: 220$$ $$kV/ 25$$ $$kV,$$ $$90$$ $$MVA,$$ $$X=12$$%
$$Line$$ $$1: 220$$ $$kV,$$ $$X= 150$$ $$ohms$$ GATE EE 2010 Power System Analysis - Per Unit System Question 6 English

Choose $$25$$ $$kV$$ as the base voltage at the generator $$G1,$$ and $$200$$ $$MVA$$ as the $$MVA$$ base. The impedance diagram is

A
GATE EE 2010 Power System Analysis - Per Unit System Question 6 English Option 1
B
GATE EE 2010 Power System Analysis - Per Unit System Question 6 English Option 2
C
GATE EE 2010 Power System Analysis - Per Unit System Question 6 English Option 3
D
GATE EE 2010 Power System Analysis - Per Unit System Question 6 English Option 4
4
GATE EE 2006
MCQ (Single Correct Answer)
+2
-0.6
A generator is connected through a $$20$$ MVA, $$13.8/138$$ kV step up transformer, to a transmission line. At the receiving end of the line a load is supplied through a step down transformer of $$10$$ MVA, $$138/69$$ kV rating. A $$0.72$$ p.u. load, evaluated, on load side transformer ratings as base values of $$10$$ MVA and $$69$$ kV in load circuit, the value of the load (in per unit) in generator circuit will be
A
$$36$$
B
$$1.44$$
C
$$0.72$$
D
$$0.18$$

GATE EE Subjects

Browse all chapters by subject