1
GATE EE 2006
MCQ (Single Correct Answer)
+2
-0.6
A $$3$$ phase, $$10$$ $$kW$$, $$400$$ $$V,$$ $$4$$ pole, $$50$$ $$Hz$$, star connected induction motor draws $$20$$ A on full load. Its no load and blocked rotor test data are given below.
No Load Test: $$400V$$ $$6A$$ $$1002W$$
Blocked Rotor Test: $$90V$$ $$15A$$ $$762W$$
Neglecting copper loss in No Load Test and core loss in Blocked Rotor Test, estimate motor's full load efficiency.
No Load Test: $$400V$$ $$6A$$ $$1002W$$
Blocked Rotor Test: $$90V$$ $$15A$$ $$762W$$
Neglecting copper loss in No Load Test and core loss in Blocked Rotor Test, estimate motor's full load efficiency.
2
GATE EE 2005
MCQ (Single Correct Answer)
+2
-0.6
Under no load condition, if the applied voltage to an induction motor is reduced
from the rated voltage to half the rated value,
3
GATE EE 2005
MCQ (Single Correct Answer)
+2
-0.6
A three-phase cage induction motor is started by direct-on-line (DOL) switching
at the rated voltage. If the starting current drawn is 6 times the full load current,
and the full load slip is 4%, the ratio of the starting developed torque to the full
load torque is approximately equal to
4
GATE EE 2005
MCQ (Single Correct Answer)
+2
-0.6
Assertion [a]: Under V/f control of induction motor, the maximum value of the developed torque remains constant over a wide range of speed in the subsynchronous region.
Reason [r]: The magnetic flux is maintained almost constant at the rated value by keeping the ratio V/f constant over the considered speed range.