1
GATE EE 2017 Set 1
MCQ (Single Correct Answer)
+1
-0.3
A $$3$$-bus power system is shown in the figure below, where the diagonal elements of $$Y$$-bus matrix are: $${Y_{11}} = - j12\,pu,\,\,\,{Y_{22}} = - j15\,pu\,\,$$ and $$\,{Y_{33}} = - j7\,pu.$$ GATE EE 2017 Set 1 Power System Analysis - Load Flow Studies Question 23 English

The per unit values of the line reactance's $$p, q$$ and $$r$$ shown in the figure are

A
$$p = - 0.2,\,\,q = - 0.1,\,\,r = - 0.5$$
B
$$p = 0.2,\,\,q = 0.1,\,\,r = 0.5$$
C
$$p = - 5,\,\,q = - 10,\,\,r = - 2$$
D
$$p = 5,\,\,q = 10,\,\,r = 2$$
2
GATE EE 2016 Set 1
Numerical
+1
-0
The magnitude of three-phase fault currents at buses A and B of a power system are 10 pu and 8 pu, respectively. Neglect all resistances in the system and consider the pre-fault system to be unloaded. The pre-fault voltage at all buses in the system is 1.0 pu. The voltage magnitude at bus B during a three-phase fault at bus A is 0.8 pu. The voltage magnitude at bus A during a three-phase fault at bus B in pu, is __________.
Your input ____
3
GATE EE 2016 Set 1
MCQ (Single Correct Answer)
+1
-0.3
In a 100 bus power system, there are 10 generators. In a particular iteration of Newton Raphson load flow technique (in polar coordinates), two of the PV buses are converted to PQ type. In this iteration.
A
the number of unknown voltage angles increases by two and the number of unknown voltage magnitudes increases by two.
B
the number of unknown voltage angles remains unchanged and the number of unknown voltage magnitudes increases by two.
C
the number of unknown voltage angles increases by two and the number of unknown voltage magnitudes decreases by two.
D
the number of unknown voltage angles remains unchanged and the number of unknown voltage magnitudes decreases by two
4
GATE EE 2015 Set 2
MCQ (Single Correct Answer)
+1
-0.3
A $$3$$-bus power system network consists of $$3$$ transmission lines. The bus admittance matrix of the uncompensated system is
$$\left[ {\matrix{ { - j6} & {j3} & {j4} \cr {j3} & { - j7} & {j5} \cr {j4} & {j5} & { - j8} \cr } } \right]\,pu$$
If the shunt capacitance of all transmission lines is $$50$$% compensated, the imaginary part of the $$3$$rd row $$3$$rd column element (in $$pu$$) of the bus admittance matrix after compensation is
A
$$-j7.0$$
B
$$-j8.5$$
C
$$-j7.5$$
D
$$-j9.0$$