GATE EE 2008
MCQ (Single Correct Answer)
+1
-0.3
It is desired to measure parameters of $$230$$ $$V/115$$ $$V,$$ $$2$$ $$kVA$$, single-phase transformers. The following watt-meters are available in a laboratory:
$${W_1}:250\,\,V,\,\,\,10\,\,A,\,\,\,\,\,\,$$ Low Power Factor
$${W_2}:250\,\,V,\,\,\,5\,\,A,\,\,\,\,\,\,$$ Low Power Factor
$${W_3}:150\,\,V,\,\,\,10\,\,A,\,\,\,\,\,\,$$ High Power Factor
$${W_4}:150\,\,V,\,\,\,5\,\,A,\,\,\,\,\,\,$$ High Power Factor

The watt-meters used in open circuit test and short circuit test of the transformer will respectively be

A
$${W_1}$$ and $${W_2}$$
B
$${W_2}$$ and $${W_4}$$
C
$${W_1}$$ and $${W_4}$$
D
$${W_2}$$ and $${W_3}$$
2
GATE EE 2007
MCQ (Single Correct Answer)
+1
-0.3
In a transformer, zero voltage regulation at full load is
A
not possible
B
possible at unity power factor load
C
possible at leading power factor load
D
possible at lagging power factor load
3
GATE EE 2006
MCQ (Single Correct Answer)
+1
-0.3
In transformers, which of the following statements is valid?
A
In an open circuit test, copper losses are obtained while in short circuit test, core losses are obtained.
B
In an open circuit test, current is drawn at high power factor.
C
In a short circuit test, current is drawn at zero power factor
D
In an open circuit test, current is drawn at low power factor.
4
GATE EE 2005
MCQ (Single Correct Answer)
+1
-0.3
Which three-phase connection can be used in a transformer to introduce a phase difference of 30° between its output and corresponding input line voltages
A
Star - Star
B
Star - Delta
C
Delta - Delta
D
Delta - Zigzag