1
GATE EE 2005
MCQ (Single Correct Answer)
+2
-0.6
A $$1000$$ $$kVA,$$ $$6.6$$ $$kV,$$ $$3$$-phase star connected cylindrical pole synchronous generator has a synchronous reactance of $$20\Omega .$$ Neglect the armature resistance and consider operation at full load and unity power factor.

The power angle is close to

A
$$13.9$$ degrees
B
$$18.3$$ degrees
C
$$24.6$$ degrees
D
$$33.0$$ degrees
2
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
The synchronous speed for the seventh space harmonic $$mmf$$ wave of a $$3$$-phase, $$8$$ pole, $$50$$ $$Hz$$ induction machine is
A
$$107.14$$ rpm in forward direction
B
$$107.14$$ rpm in reverse direction
C
$$5250$$ rpm in forward direction
D
$$5250$$ rpm in reverse direction
3
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
Two $$3$$-phase, $$Y$$-connected alternators are to be paralleled to a set of common bus bars. The armature has a per phase synchronous reactance of $$1.7\Omega $$ and negligible armature resistance. The line voltage of the first machines is adjusted to $$3300$$ $$V$$ and that of the second machine is adjusted to $$3200$$ $$V.$$ the machine voltages are in phase at the instant they are paralleled. Under this condition, the synchronizing current per phase will be
A
$$16.98A$$
B
$$29.41A$$
C
$$33.96A$$
D
$$58.82A$$
4
GATE EE 2004
MCQ (Single Correct Answer)
+2
-0.6
A $$400$$ $$V,$$ $$50$$ $$kVA,$$ $$0.8$$ $$pf$$ leading delta connected, $$50$$ $$Hz$$ synchronous machine has a synchronous reactance of $$2$$ $$ohm$$ and negligible armature resistance. The friction and windage losses are $$2$$ $$kW$$ and the core loss is $$0.8$$ $$kW.$$ The shaft is supplying $$9$$ $$kW$$ load at a power factor of $$0.8$$ leading. The line current drawn is
A
$$12.29A$$
B
$$16.24A$$
C
$$21.29A$$
D
$$36.88A$$